PINNED ZXD2400 Old + New 0-60V 0-50A Power Supply & Charger

Power wheelchair board for REAL info!

POWERCHAIR MENU! www.wheelchairdriver.com/powerchair-stuff.htm

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 05 Apr 2024, 13:24

shirley_hkg wrote:

If so, self calibration failed. Prepare a piece of thick wire to short the output, and redo the self calibration again. (Turn it on, press 3 seconds to shut it down , then press 15 seconds to power it up and wait till you see the first left WHITE ZERO, follow the screen to finish .)
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby Furio » 05 Apr 2024, 16:51

Hi,

During power on, it displays set voltage and current but when switching on, zero voltage is displayed.
Anyway, tomorrow I will carry out the procedure as Shirley-hkg suggested.
Furio
 
Posts: 193
Joined: 24 Dec 2011, 18:10
Location: India


Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby Furio » 06 Apr 2024, 10:28

Self calibration could not be done as the white zero didn't appear. While tinkering, I noticed the eprom settings 52 & 53 of voltage and current, altered to 120v and 25amps. These are now set at 60v and 40amp. Yet there is no voltage at the o/p terminals.If anybody posts recommended settings of eprom I can compare with those and reset.
Furio
 
Posts: 193
Joined: 24 Dec 2011, 18:10
Location: India

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 06 Apr 2024, 12:52


Would you take a video how it turns on, and upload to youtube ?
Take another video that shows it won't go to self calibration too .
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby Burgerman » 06 Apr 2024, 17:25

Do you mean 60V and 50A? Thats what it should be as stock.
User avatar
Burgerman
Site Admin
 
Posts: 69922
Joined: 27 May 2008, 21:24
Location: United Kingdom

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby Furio » 09 Apr 2024, 08:05

Hi shirley-hkg ,

I got into auto calibration mode after changing the password, but ended up with error 001as happened to LRobbins though I have not changed the fans as he did. So now???
Furio
 
Posts: 193
Joined: 24 Dec 2011, 18:10
Location: India

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 09 Apr 2024, 08:40


Maybe we can try to increase the fan loads.
Bigger fans ?
Pair another fan to the original one ?
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby Burgerman » 09 Apr 2024, 08:56

Maybe a fan has failed or its connection isnt good?
Strange coincidence though. Same error etc.
User avatar
Burgerman
Site Admin
 
Posts: 69922
Joined: 27 May 2008, 21:24
Location: United Kingdom

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby Furio » 09 Apr 2024, 09:59

The existing fans are the original ones and both are working.There was never a rough handling. It is impossible to add another one. There might be some software solution. czy

My ZXD2400 version is 3.17
Furio
 
Posts: 193
Joined: 24 Dec 2011, 18:10
Location: India

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 09 Apr 2024, 10:10

shirley_hkg wrote:
Got in touch with the modification guy , who said it's hard to say without visual .

Would you take a video how it turns on, and upload to youtube ?
Take another video that shows it won't go to self calibration too .
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 09 Apr 2024, 16:17

Furio wrote:The existing fans are the original ones and both are working.There was never a rough handling. It is impossible to add another one.


Pair a fan to the original one to increase load , or swap with a fan with bigger amp.
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 18 Jul 2024, 13:27

Newest version now with English menu and adjustable fan speed.

Attachments
IMG-20240718-WA0028.jpg
IMG-20240718-WA0029.jpg
IMG-20240718-WA0030.jpg
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 18 Jul 2024, 13:28

cheers
Attachments
IMG-20240718-WA0031.jpg
IMG-20240718-WA0032.jpg
IMG-20240718-WA0033.jpg
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 18 Jul 2024, 13:38

cheers
Attachments
IMG-20240718-WA0035.jpg
IMG-20240718-WA0034.jpg
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby LROBBINS » 18 Jul 2024, 15:27

That looks very complete. But, what is Li-Ion Mode?
LROBBINS
 
Posts: 5774
Joined: 27 Aug 2010, 09:36
Location: Siena, Italy

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby Burgerman » 19 Jul 2024, 08:52

Look at the very clear Lead settings in the picture.

I EXPECT that lion is just another set of CC/CV/FLOAT or no float preferable on lithium with you able to set up an aditional bunch of settings.

So for lead you might set 30A, CV 28.80V and terminates at 0.2A and sits at 27V float
For Lithium Ion you might set 45A,CV 29.4V and termination at x mins CV or at maybe 0.8A. for e.g. No float.
User avatar
Burgerman
Site Admin
 
Posts: 69922
Joined: 27 May 2008, 21:24
Location: United Kingdom

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby ex-Gooserider » 22 Jul 2024, 23:47

Looks really nice - is that the 'fancy' case or a modified version of the 'stock' case? I didn't see any outputs...

Roughly how much shipped to US, (preferably in $USD?)

ex-Gooserider
T-5, ASIA-B
Jazzy 1100
Jazzy Select 6
Quickie Q-7
Invacare Mariner
Want to make / get a better chair, ideally one that stands.
User avatar
ex-Gooserider
 
Posts: 6197
Joined: 15 Feb 2011, 06:17
Location: Billerica, MA. USA

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby Burgerman » 23 Jul 2024, 00:38

Thats how it comes.

And a bargain at 4x the actual price. At least it is in most of the world where its a 3KW capable device. Theres nothing like this for a solid reliable well build device at this sort of power. Or even 1/3rd of that.

0-50A, 0-60v, 2 stage as power supply, 3 stage as lead battery charger, 2 stage as lithium ion charger, adjustable transittion or end currents, whats not to love? Only the fact that all this stuff is controlled with 1 push, turn knob. Takes a little figuring out. Then you get it. Press, wait for things to flash or change, press again etc.

And a 3KW capable supply this compact is quite amazing really. In the US you wll be limited to 25A instead of 50 I think. But even so still good.
User avatar
Burgerman
Site Admin
 
Posts: 69922
Joined: 27 May 2008, 21:24
Location: United Kingdom

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 23 Jul 2024, 04:23

Try to add notation to its 3-stage charger mode.

Attachments
IMG-20240723-WA0004.jpg
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 23 Jul 2024, 08:23

Looks really nice - is that the 'fancy' case or a modified version of the 'stock' case? I didn't see any outputs...
Stock case version now comes with pair of output posts and a XT90 male connector for heavy loads.

Attachments
IMG-20230528-WA0004.jpg
IMG-20230528-WA0005.jpg
mmexport1721718907979.jpg
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 23 Jul 2024, 10:09

If you don't mind 50% increase in size & weight, the "fancy" aluminum version is also available.

Output will be completed with power posts, XT90, and Anderson SB50 cheers connector(from shirl _hkg exclusively).

You may also have a large 3.2" screen (stock is 2..4 inch).

Attachments
mmexport1721725500247.jpg
1684208306725.jpg
IMG-20240723-WA0008.jpg
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby Burgerman » 23 Jul 2024, 10:21

How much for each one?

Thanks!

I prefer the last one. The laid down on its side one.
User avatar
Burgerman
Site Admin
 
Posts: 69922
Joined: 27 May 2008, 21:24
Location: United Kingdom

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 23 Jul 2024, 10:23

You may also order a twin supply unit.


https://youtube.com/shorts/vFLtcv-3pZ0? ... y9JQYBitlu
Attachments
IMG-20240723-WA0010.jpg
IMG-20240723-WA0009.jpg
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby Burgerman » 23 Jul 2024, 10:40

Err, how do I power a 6KW power supply?

Or you just have to be careful what power you choose.

3.1KW is all the outlets can handle technically. Although you can do a bit more if you dont care! Actually in my room its all double sockets on a 30A ring main so it would be OK I suppose as its got 2 AC plugs..
User avatar
Burgerman
Site Admin
 
Posts: 69922
Joined: 27 May 2008, 21:24
Location: United Kingdom

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 23 Jul 2024, 10:52

Burgerman wrote:Err, how do I power a 6KW power supply?
I didn't think about that. banghead

Burgerman wrote:I prefer the last one. The laid down on its side one.
I will check it out.
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 23 Jul 2024, 11:02

We are in deflation, and the new prices went down.

Stock unit : $230 / £180
Fancy aluminum unit : $285 / £220

10 days shipping included. Accept paypal.
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby Burgerman » 23 Jul 2024, 11:45

So in pounds, at current rate, inc shipping to UK how much for the laid down fancy one? Same price? (£285)
User avatar
Burgerman
Site Admin
 
Posts: 69922
Joined: 27 May 2008, 21:24
Location: United Kingdom

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby shirley_hkg » 23 Jul 2024, 13:15

£5 if any.
Seems no room for SB50. Be prepared to swap out the XT90, if an Anderson were to be installed.

Still checking for stock.

Attachments
IMG-20240723-WA0014.jpg
shirley_hkg
 
Posts: 4483
Joined: 31 Dec 2010, 13:42

Re: ZXD2400 modification guild 3Kw 0-60V 0-50A

Postby Burgerman » 23 Jul 2024, 13:37

I can do that. Or just make a XT90 to anderson connector on a short cable.
User avatar
Burgerman
Site Admin
 
Posts: 69922
Joined: 27 May 2008, 21:24
Location: United Kingdom